I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Brian,
I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately.
Yes that is permited. You will have to comply with 210.5.
Don
 