B brian@sutherland Member Mar 8, 2007 #1 I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately.
I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 8, 2007 #2 Brian, I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately. Click to expand... Yes that is permited. You will have to comply with 210.5. Don
Brian, I am specifying ASCO 917 contactors. Can I mix 120V and 277V lighting on the same contactor? As I understand the contacts are rated appropriately. Click to expand... Yes that is permited. You will have to comply with 210.5. Don