S steve holt Member Location Hawaii Saturday at 12:34 PM #1 Do lighting control panels that do not have over current protection, but just relays, require dedicated space?
Do lighting control panels that do not have over current protection, but just relays, require dedicated space?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Saturday at 2:06 PM #2 In my opinion, they do.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Saturday at 4:56 PM #3 don_resqcapt19 said: In my opinion, they do. Click to expand...
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Today at 9:38 AM #4 Let's be clear about terms. Do lighting control panels require working clearance (i.e., in front, to allow for safe working)? Yes. Do they require dedicated equipment space (i.e., above, for future installation of conduits)? No.
Let's be clear about terms. Do lighting control panels require working clearance (i.e., in front, to allow for safe working)? Yes. Do they require dedicated equipment space (i.e., above, for future installation of conduits)? No.