160904-1444 EDT
There is far too much conjecture here and too little measured quantitative data.
I just ran a comparative experiment with a 100 W incandescent and the CREE LED I previously mentioned.
The voltage was adjusted by a Variac (actually a Powerstat) the light intensity was measured with a 66 year old GE light meter (probably a selenium photocell).
The results in volts and footcandles are:
Also shown are % change in intensity.
(foot candles)
CREE LED
120, 40 --- 100, 39+ ---- 80, 38.5
100 W incandescent
120, 55 --- 100, 48 ----- 80, 40
(% change)
CREE LED
120, 0% ---- 100, 0.5% --- 80, 3.7%
100 W incandescent
120, 0% ---- 100, 12% ---- 80, 27%
A casual observer watching the LED or incandescent will unlikely see the change in LED intensity from 120 to 100 V. But, will certainly see the incandescent change.
In a very tightly controlled experiment it probably can be shown that the observer can detect the change in the LED intensity even though the observer does not realize they have detected the change.
If the same observer looks separately at the light from the bulbs at 120 V excitation, and does not have them for side by side comparison, goes outdoors, comes back inside, rests for a while, has no other lights for comparison, the lights are now excited at 100 V, then with almost total certainty that observer will not detect a change in the LED light output, and may or may not detect the change in the incandescent intensity.
In JDB3's situation did changing to LEDs simply mask the problem, and there is still a voltage change at the bulb, or did the change in power load eliminate the original cause of the dimming? We won't know without investigation of the light kit or input wiring.