As such, there is no need to bond the GES via a GEC or GEC tap to the grounded conductor (neutral). The GES is already bonded to the service neutral at another point or points, and the GEC(s) are sized based on the ungrounded conductors size(s). The service is sized to deliver the calculated load without the additional energy provided by the PV System, so it stands to reason the GES is already sufficient. However, the disconnect must have neutral-to-enclosure bond (albeit a jumper, which is not to be confused as a Main or System Bonding Jumper) to ground the enclosure and establish an EGC for the PV side.