I am working on a 1 megawatt system that involves a line side tap to a fused disc. switch. My question is should the tap conductors be run to the line or load side of the fused disc.?
Line side always goes toward the utility source.I am working on a 1 megawatt system that involves a line side tap to a fused disc. switch. My question is should the tap conductors be run to the line or load side of the fused disc.?
I am working on a 1 megawatt system that involves a line side tap to a fused disc. switch. My question is should the tap conductors be run to the line or load side of the fused disc.?
Another rule of thumb, is that the hinge of the disconnect blade should point toward the inverter. This way, the side that remains energized when the disconnect is open, is the side connected to the line side terminals. The AC side of the inverter will de-energize on loss of utility power. The DC side will eventually de-energize when the capacitors bleed down, in contrast from the PV side which remains energized as long as there is sunlight.
Another rule of thumb, is that the hinge of the disconnect blade should point toward the inverter. This way, the side that remains energized when the disconnect is open, is the side connected to the line side terminals. The AC side of the inverter will de-energize on loss of utility power. The DC side will eventually de-energize when the capacitors bleed down, in contrast from the PV side which remains energized as long as there is sunlight.
It's actually the same rule of thumb that I posted, only worded differently.Great rule of thumb.
Line side always goes toward the utility source.
Load side always goes away from the utility source.
I am reading the question a little differently - not really sure what the op is asking. Is the switch in question the normal/existing service diconnect? If so, it wouldn't be a line side connection if you connect to the load side.....
I had a couple different responses typed up reading a few times with different understandings. Then I realized it didn't matter which scenario was in play because the utility (POCO) is always on the line side.Ok reread, I get it. That's a common question. I was going "the other direction".
It's actually the same rule of thumb that I posted, only worded differently.
Carultch's rule of thumb applies on the dc and ac sides of an inverter. That makes it a great mnemonic device for people attending beginning/intermediate solar classes or new solar apprentices.
I can understand someone being confused which way to wire the AC side switch with its bi directional nature but if someone has problems figuring it out on DC side I would say that no mnemonic is going to help.
I am a bit concerned of the OP working a megawatt system & does not know line from load.
Except there is no load. With a parallel power system, you have two sources. This question is fairly common even among experienced electrical engineers and electricians when they first encounter an interactive system.
Except there is no load. With a parallel power system, you have two sources. This question is fairly common even among experienced electrical engineers and electricians when they first encounter an interactive system.
Interesting -- a megawatt system in parallel with utility to serve a structure did not get that from the OP -- generally I would assume the megawatt system is serving the utility such as a solar farm.
Line side taps are not allowed only line side connections