pv_n00b

Senior Member
Location
CA, USA
Except there is no load. With a parallel power system, you have two sources. This question is fairly common even among experienced electrical engineers and electricians when they first encounter an interactive system.

True, but I would hope the first encounter someone had with an interactive PV system was not also a 1MW project. ;)
 

pv_n00b

Senior Member
Location
CA, USA
I am working on a 1 megawatt system that involves a line side tap to a fused disc. switch. My question is should the tap conductors be run to the line or load side of the fused disc.?

Just a heads up, you will get dope slapped by some for calling it a line side tap. :blink:

It's a supply side or line side interconnection.
 

Smart $

Esteemed Member
Location
Ohio
Gimme a break......From now on, no field jargon is allowed :roll:
I agree with giving us a break... but technically it is not just field jargon. How often are wire-type interconnect conductors of the size required for the entire service (i.e. splice rather than tap). Technically, service tap conductors are not defined. So one cannot apply the load side tap conductor definition.
 
I agree with giving us a break... but technically it is not just field jargon. How often are wire-type interconnect conductors of the size required for the entire service (i.e. splice rather than tap). Technically, service tap conductors are not defined. So one cannot apply the load side tap conductor definition.

And there is 230.46: service conductors may be spliced or tapped.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
True, but I would hope the first encounter someone had with an interactive PV system was not also a 1MW project. ;)

On the other hand, if one is looking for someone to do the AC side of a 1MW system, and the choices are an electrical contractor who has significant experience doing non-interactive hookups of the same power level vs. one who has a lot of solar experience but at much lower power levels, it'd probably be wise to go for the former. No?
 

Carultch

Senior Member
Location
Massachusetts
On the other hand, if one is looking for someone to do the AC side of a 1MW system, and the choices are an electrical contractor who has significant experience doing non-interactive hookups of the same power level vs. one who has a lot of solar experience but at much lower power levels, it'd probably be wise to go for the former. No?

If that is the case, and it were up to me, I'd hire the former to do most circuits 100A and greater and/or medium voltage where applicable, and I'd hire the latter to do the general array construction and wiring.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
If that is the case, and it were up to me, I'd hire the former to do most circuits 100A and greater and/or medium voltage where applicable, and I'd hire the latter to do the general array construction and wiring.

Exactly. And the former guy is the one who would ask the OP's question.
 

pv_n00b

Senior Member
Location
CA, USA
On the other hand, if one is looking for someone to do the AC side of a 1MW system, and the choices are an electrical contractor who has significant experience doing non-interactive hookups of the same power level vs. one who has a lot of solar experience but at much lower power levels, it'd probably be wise to go for the former. No?

It would be wiser to go with another choice. I'm not big on answering false dichotomy setups, which of these two bad choices are the least bad.
If I'm the developer of a 1MW PV project then I would hire people with experience in MW level PV systems. Blade direction is PV 101 level stuff. It's a legitimate question from someone getting started and maybe doing their first residential install. From someone doing a 1MW interconnection it makes me wonder what other PV basics they do not know.
 
Last edited:

bob52

Member
Location
pittsfield ma
thanks for your response

thanks for your response

Actually I am in agreement with the answers given unfourtionatley the Inspector of wires was not. I am hoping seeing all these responses will help to make the right decision on weather I have to rewire my disc.
It would be wiser to go with another choice. I'm not big on answering false dichotomy setups, which of these two bad choices are the least bad.
If I'm the developer of a 1MW PV project then I would hire people with experience in MW level PV systems. Blade direction is PV 101 level stuff. It's a legitimate question from someone getting started and maybe doing their first residential install. From someone doing a 1MW interconnection it makes me wonder what other PV basics they do not know.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Actually I am in agreement with the answers given unfourtionatley the Inspector of wires was not. I am hoping seeing all these responses will help to make the right decision on weather I have to rewire my disc.

I'm a bit lost here. Are you saying that your inspector wants the inverter output conductors to be wired to the line side of your AC disco?
 

310 BLAZE IT

Senior Member
Location
NJ
Similar to how I've asked how to know which side to call primary vs secondary of a backfed transformer. Obviously I know what primary and secondary mean in general, but when aren't building a conventional system where power only flows from the utility, it isn't as simple to choose your vocabulary.
Someone on solar cmp please define these terms I find it very frustrating to clarify this to anyone who I'm talking to



Sent from my SM-N920V using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Someone on solar cmp please define these terms [primary and secondary of transformer] I find it very frustrating to clarify this to anyone who I'm talking to.
Unfortunately, there is no uniform way to look at this. Some schools of thought call the higher voltage side of a transformer the "primary" irrespective of the direction of current flow. Others consider the "uphill" side of current flow to be the primary.

To try to avoid confusion I usually refer to them as the high and low voltage sides of the transformer, which works unless the transformer is a uniform voltage isolation transformer, in which case all bets are off. :D
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Unfortunately, there is no uniform way to look at this. Some schools of thought call the higher voltage side of a transformer the "primary" irrespective of the direction of current flow. Others consider the "uphill" side of current flow to be the primary.

To try to avoid confusion I usually refer to them as the high and low voltage sides of the transformer, which works unless the transformer is a uniform voltage isolation transformer, in which case all bets are off. :D
For many purposes the most useful way to designate the primary is that it is the winding which is first energized when the transformer is connected.
Not the first one to be connected, but the first energized and therefore the winding that supplies the inrush and magnetizing current.
 

JasonC

Member
Location
N. Andover MA
Lets Break this down simply.

Lets Break this down simply.

I am working on a 1 megawatt system that involves a line side tap to a fused disc. switch. My question is should the tap conductors be run to the line or load side of the fused disc.?

Lets remember all the equipment is still energized even when the PV is not producing power.

"line side tap to a fused disc." So you are energizing a set of conductors prior to the OCPD associated with the Feeding conductors (Between the meter and main.)

"should the tap conductors be run to the line or load side of the fused disc.?" Those conductors must go the line side of the Solar disconnect, if not your going to get surprised when you go to replace the fuses for the PV array as the fuses will be energized as well as the blades.

Think about the next person that is going to work in that equipment that has never seen solar.
 