Does anyone know if there is a limit in the NEC on the length that you can install
E etechman Member Dec 1, 2009 #1 Does anyone know if there is a limit in the NEC on the length that you can install
qcroanoke Sometimes I don't know if I'm the boxer or the bag Location Roanoke, VA. Occupation Sorta retired........ Dec 1, 2009 #2 etechman said: Does anyone know if there is a limit in the NEC on the length that you can install Click to expand... I don't think there is but code book is at the office. I do know once you get to six foot you must pull an equipment ground.
S SEO Senior Member Location Michigan Dec 1, 2009 #3 If you are asking about LFNC look at section 356.10 Uses Permitted (5) lengths longer than (6 ft) for LFNC-B shall be permitted where secured in accordance with 356.30. It doesn't have a max length where secured per section 356.3. Last edited: Dec 1, 2009
M macmikeman Senior Member Location Planet macmikeman Dec 1, 2009 #4 If it is used to wire an outdoor spa it is limited to 6' lengths. 680.42 (A)(1) That paragraph can sometimes get mistakenly used to dictate 6' length limitations for installation in other areas. "I know I read it somewhere...."
E etechman Member Dec 2, 2009 #5 Thanks everyone, i read the same but some people just can't understand