Does anyone know if there is a limit in the NEC on the length that you can install

I don't think there is but code book is at the office. I do know once you get to six foot you must pull an equipment ground.
 
If you are asking about LFNC look at section 356.10 Uses Permitted (5) lengths longer than (6 ft) for LFNC-B shall be permitted where secured in accordance with 356.30. It doesn't have a max length where secured per section 356.3.
 
Last edited:
If it is used to wire an outdoor spa it is limited to 6' lengths. 680.42 (A)(1)

That paragraph can sometimes get mistakenly used to dictate 6' length limitations for installation in other areas. "I know I read it somewhere...."
 