1. If the protective device is not designed for personnel protection with a threshold of approximately 6ma, it is not technically a GFCI under US terminology. It can be called GFP (Ground Fault Protection) or simply a GF detecting device. In the EU it will usually called an RCD (Residual Current Detector). A device in a panel with 100ma sensitivity is not, by definition, a GFCI.
2. You are not likely to find such a list.
The most common and hard to track down cause of current leakage to grounded metal in an appliance is capacitive coupling between wires (as in a motor) or heating elements (as in a defrost heater) and ground. This is not designed in and (obviously) in some cases is not adequately tested for as part of the approval process for a design. Some capacitve coupling is unavoidable, so the goal would have to be to reduce it to a level which will not trip a GF detector.
3. In some cases there is actually inadequate insulation which can produce current leakage and this low insulation resistance to DC can be detected with an ohmmeter or a megger.
4. Air conditioners will not necessarily have a high leakage current and there are no typical values associated with a particular size unit.
Stoves and ovens with a spark igniter or heating appliances with a spark igniter use a high voltage spark from an internal insulated electrode to an internal grounded electrode, with the high voltage being produced by an internal power supply driven from AC. This arc current can in some cases be interpreted as ground fault current in a detector in the supply to the appliance. Again, it is essentially the result of inadequate attention to GF tripping in the design of the unit, but the results in any particular situation can also vary with the way in which the appliance is grounded and the susceptibility of the GF detector to high frequency arc current.