Can you clarify few things so that we can all learn from this matter?
1. How did a guy who didn't know what he was doing end up in this situation-is he a qualified licensed electrician, if not, how did he end up in this panel and do you know exactly what he did to cause the flash?
2. You said that the panel was compliant, but how old was it and has it been maintained to manufacturers standards?
1. Just a maintenance guy who tried to check voltage and used a crappy meter set to ohms. The thing exploded. The meter's fuse didn't even blow.
2. Probably about 5 years old, and fairly maintained.
I am not an advocate of people working around electricity that don't know what they are doing. Makes for a dangerous situation. Also not a fan of crappy test equipment. Makes for a
potentially dangerous situation. I've seen this in plants before, where there are only a few people that understand electricity and controls but there are times when those people are not
around. And then the poor bastard with the non working machine takes a stab at it. Yes we do need to establish whom is a qualified worker. The reality is that in a lot of plants there
will be pressure to get things running and non qualified personnel may try to troubleshoot an electrical problem. Usually these people will own some sort of cheap meter. Which is exactly
what happened. That said, if the meter was set correctly everything would have been ok. And a better quality meter would have just blown it's fuse.
Also pertaining to your 1st question; I have been working with equipment and controls for many years and it is rare to see a licensed electrician in a equipment tech sort of job. Most of the
licensed guys I have met don't really know controls. So to me, not having a license doesn't necessarily mean someone doesn't know what he or she is doing.