Panel information:
150 amp MCB
208/120
3 Phase
Phase A Load = 14.5 KVA
Phase B Load = 11.5 KVA
Phase C Load = 11.9 KVA
Connected KVA = 37.9
Dem. Kva = 26.2
Dem. Amps = 72.8
I have 17 additional circuits at 12 amps a piece per equipment name tag to add. My calculations appear to show to much load being added for a 150 main breaker.