Re: LOAD CALCULATIONS FOR 120/240, 3 PHASE DELTA SERVICE???
At the risk of being boring, this is what I wrote in our training module on transformers.
LOADING AND CONVERSIONS
Splitting the load on open delta and closed delta banks is not intuitive; however it is simple to do. The following formulae and examples show how to split the load on open delta and closed delta banks, how to convert from one to the other, and how to convert measured amperes for a service to load open delta and closed delta banks.
Loading an open delta bank
Place all of the single phase load on the lighting (larger) transformer and split the three phase load by multiplying it by the inverse of the square root of three (.577) to add to the lighter and the kicker (smaller).
Example:
75 kVA of single phase and 30 kVA of three phase load.
Lighter Kicker
Single phase 75.0 kVA 0.0 kVA
Three phase 17.3 kVA 17.3 kVA
Totals 92.3 kVA 17.3 kVA
Loading a closed delta bank
Split the single phase load by placing two thirds on the lighting (larger) transformer and one third on the kicker (smaller) transformer. Split the three phase load by placing one third on the lighter and each of the kickers.
Example:
30 kVA of single phase and 60 kVA of three phase load.
Kicker Lighter Kicker
Single phase 10.0 kVA 20.0 kVA 10.0 kVA
Three phase 20.0 kVA 20.0 kVA 20.0 kVA
Totals 30.0 kVA 40.0 kVA 30.0 kVA
Converting from an open to a closed delta
1. Using test data, subtract the kicker (smaller transformer) load from the lighter (larger transformer) load to get the total single phase load.
2. Multiply the kicker load by the square root of three to get the three phase load.
Use the results for calculating the loading for a closed delta bank.
Example:
From a test on an open delta bank, the lighter has 60 kVA and the kicker has 21.6 kVA of load.
Subtracting the kicker load from the lighter
60 kVA ? 21.6 kVA = 38.4 kVA
Multiply the kicker load by the square root of three
(Sq. Rt. 3)(21.6 kVA) = 37.4 kVA
Your loads are 38.4 kVA single phase and 37.4 kVA three phase.
Converting from a closed to an open delta
1. Using test data, subtract the kicker (smaller transformer) load from the lighter (larger transformer) load, then multiply the resultant by three to get the total single phase load.
2. Subtract one third of the single phase load from the kicker, then multiply the resultant by three to get the three phase load.
Use the results for calculating the loading for an open delta bank.
Example:
From a test on an open delta bank, the lighter has 76.8 kVA and the kickers have 64.8 kVA of load each.
Subtracting a kicker load from the lighter and multiplying by three
(3)(76.8 kVA ? 64.8 kVA) = 36.0 kVA
Subtracting one third of the single phase load from the kicker and then multiplying the resultant by three
(3)(64.8 kVA ? 12.0 kVA) = 158.4 kVA
Your loads are 36.0 kVA single phase and 158.4 kVA three phase.
This, of course, could not be served with an open delta bank because of the size of the loads.