Re: LOAD CALCULATIONS FOR 120/240, 3 PHASE DELTA SERVICE???
I came in late....
Is it 240V delta, corner ground
or 240V delta with a high leg??
That's important...
If it's corner ground...you can only use Phases A,C for single phase loads, because phase B is grounded.
If it's a high leg, you can only use the A,C for single phase loads, because the B phase is at 208V.
Mainly this system is for three phase loads, however for the high leg, 240/1ph loads are ok to use