mdshunk said:
That's just strange. They publish the current draw of the notification appliances for a reason.
I know it seems strange at first. We resisted the idea initially, but through some heavy consulting with electrical engineers, fire alarm code experts, etc. we found that the battery performance variables (age, voltage drop over time of draw-down, etc.) meant we were not getting accurate answers as to whether the batteries would actually perform.
We also have the luxury, I guess, of being on the enforcement side, so our "billing" needs are different than for an EC. Setting up the 24 hour jobs is sometimes difficult, but most systems in our area report A/C Fail as well as low battery, so many buildings can go unoccupied at night as long as someone is on call to run in and throw the breaker if the low battery alarm comes in. Some buildings will throw the breaker 4 hours before we arrive, coordinated with the test team. Then we witness the system running on battery, hit the alarm to test it (5 or 15 min), the test crew verifys the function of the notifications devices, they then restore A/C and the test team goes to work: device by device.
Please also keep in mind we most often use this where the design calcs are not available to do the math on battery size, so we don't even know if the batteries are big enough when they come out of the box.
For Jim (Security 101) (I don't know how to quote two posts in one answer, sorry.) No, you don't have to run the generator, the code requires 4 hours of battery if the alarm has generator back-up, just in case the gen doesn't start. So, leave the generator alone, run the alarm for four hours on battery.
Mike