boneyard
Member
- Location
- Linton, Indiana, USA
I have a 400 amp meter base on a detached garage/shop w/ it's own 200A disconnect.  I'm building a house that is located 35 feet away from meter base and separated from garage/shop by 15 feet.  I was hoping to mount another 200A disconnect beside the first (on the garage), and feed the house with that, but after I read Article 225.32, it seems I will need to mount this disconnect directly on the house.  Is this correct, or is there any other provision or exception that might allow me to mount the disconnect on a separate structure?  I'm pretty sure exception #1 doesn't apply to me since it's a residence and I don't have any maintenance or monitoring!  Thanks
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		