mpd said:cpal
I think 440.14 will result many different interpretations, my idea and your idea of readily accessible may not be the same, I think 110.26 provides a readily accessible work space, but like I said I was told I can not cite 110.26 for a air cond. disconnect.
Not always Charlie. I've gotten interpretations from them via email and I thought, this is great until I read the whole email. At the end it said something like "this is not an official interpretation just an opinion." But they are very good at what they do and they may give other information you may not have thought of. I call the NFPA a couple times a month on average.cpal said:I have to admit that I have a problem with that. But I will attempt a call to the NFPA ,but as I understand it offical interpertations are in writing.
Thanks for the input
Charlie
McDowellb said:Not always Charlie. I've gotten interpretations from them via email and I thought, this is great until I read the whole email. At the end it said something like "this is not an official interpretation just an opinion." But they are very good at what they do and they may give other information you may not have thought of. I call the NFPA a couple times a month on average.
Equipment. A general term including material, fittings, devices, appliances, luminaires (fixtures), apparatus, and the like used as a part of, or in connection with, an electrical installation.
Show me the exceptions to the words as written in the code. All electrical equipment that is likely to be worked on or tested while energized is covered by the code rule. Every electrical item that has been mentioned in this thread is electrical equipment per the Article 100 definition. Does it make an sense? NO, and that is why there is such a diversion of opinions on the issue. As I said in a previous post the CMP needs to get its head out of the sand and accept a proposal that puts reasonable limits on the application of the work space rule. However, until that happens all electrical equipment that contains energized parts and is likely to be worked on or tested while energized requires the work space. This type of code writing leads code users to start ignoring code rules because some, like this one are not usable or enforceable, and they start to think other rules are the same.110.26 (A) Working Space Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
Read the code words....all electrical equipment that is likely to be worked on while energized requires the 110.26(A) work spaces. If you don't agree show me the words that say 110.26(A) only applies if there are fuses or circuit breakers in the enclosure. There are only two things that must exist before 110.26(A) applies as it is currently written. One, it must be electrical equipment (see the Article 100 definition of equipment) and two, it must be likely that the electrical equipment will be worked on while energized. As soon as both of these conditions exist, you must provide the 110.26(A) work space. Does this code rule make any sense...of course not, but that is what the words say. The section needs a major rewrite.What needs to have the clearences as per 110.26? As stated before, if there are no fuses or circuit breakers then quite simply the clearences per 110.26 are not relevant.
In this case the disconnect (plug) does not need 110.26(A) work space as you can't work on it while energized. As soon as you unplug it it is not energized. However the receptacle in the wall does require 110.26(A) work spaces and before you say it doesn't show me the code words that say it doesn't. As far as looking at the big picture, I am only looking at the code rule as that is what we are talking about here.The disconnect (cord and plug) is not readily accessible nor does it have the clearences you speak of. I think you should really look at the big picture.
Show me in the code where it says all receptacles are required to have clearences..... That is rediculous and not the intent of the code. I emplore you to call the NFPA at 1 (617)770-3000. They will update you on the reallity of the code in regards to clearences and readily accessible.don_resqcapt19 said:Mr. McDowell,
Read the code words....all electrical equipment that is likely to be worked on while energized requires the 110.26(A) work spaces. If you don't agree show me the words that say 110.26(A) only applies if there are fuses or circuit breakers in the enclosure. There are only two things that must exist before 110.26(A) applies as it is currently written. One, it must be electrical equipment (see the Article 100 definition of equipment) and two, it must be likely that the electrical equipment will be worked on while energized. As soon as both of these conditions exist, you must provide the 110.26(A) work space. Does this code rule make any sense...of course not, but that is what the words say. The section needs a major rewrite.
In this case the disconnect (plug) does not need 110.26(A) work space as you can't work on it while energized. As soon as you unplug it it is not energized. However the receptacle in the wall does require 110.26(A) work spaces and before you say it doesn't show me the code words that say it doesn't. As far as looking at the big picture, I am only looking at the code rule as that is what we are talking about here.
Don
don_resqcapt19 said:[FONT="] Show me the exceptions to the words as written in the code. Don
[/FONT]
110.26 (A) Working Space Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
Been out of town for a few days.Jim W in Tampa said:Would a breaker lock out fix this
Mine came in today.Seems rather stupid when we all know they will never be used.Perhaps we need them on every breaker !!!!!.What if i have a panel cover with a key lock ? Does that fix anything ?Problem is in Pasco of course.I had to work on a live switch today and did not have the required space.Just how far do they want to take this foolish rule.allenwayne said:Been out of town for a few days.
Well Jim yes a breaker lock out would fix the situation if the pull out was above an a/c unit with the a/c encroaching the 110.26 requirements.If locked out then it would not be energized then working space requirements don`t come into play.110.26A states WHILE ENERGIZED !!!!!If not energized then not required to have a clear working space.If not used then it falls on the service techs shoulders.As long as it is a usable lock out we did our part.
I`ve installed 1000`s of lock outs for just this reason .We wire after a/c rough then the concrete guys pour a slab right under our disconnect then we get tagged for clearance on final.I`ve tried running the nm in the A/C chase and leaving a long tail but it usually gets cut and stolen.So I keep a large supply of lock outs around.
Is a receptactle "equipment" per the Article 100 definition?\Show me in the code where it says all receptacles are required to have clearences
If they don't like what their words say, then they should direct CMP 1 to accept one of the many proposals that have been submitted to correct this code section.That is rediculous and not the intent of the code. I emplore you to call the NFPA at 1 (617)770-3000. They will update you on the reallity of the code in regards to clearences and readily accessible.
marcb said:I think that it is time to close this thread.