Mike,
Don
I see nothing in 210.52 or 440.14 that acts as an exception to 110.26(A). The code is in conflict with it self and the rule in 110.26(A) must be revised, but CMP 1 refuses to accept any revisions. I don't apply 110.26(A) to all equipment, but if you really read the words of the section, it does apply to any and all equipment that "is likely to be worked on while energized". Give the current state of the safety practices of many in the trade, it is very likely that any and all equipment covered by this section will be worked on while energized. Remember that even using a contact type of voltage tester or other instrument is working hot. The application of this to a receptacle may be a bit of a stretch, but I have seen then replaced while the circuit was live many times...in years past I have even done that myself. If it is likely that this type of activity will take place the current code wording requires working space.So, since kitchen counters require receptacles, clearly that requirement negates the clearance requirement and allows the receptacles to be installed above a countertop. The big question in my mind is if the accessibility requirement in 440.14 supersedes 110.26, since 440.14 spells out the requirement for the AC disconnect.
Don