McDowellb said:
"I'm sooo done with this thread. I NEVER get written up for it. So you are wrong".
RickG writes:
So, what about the tech that opens the disco to check for voltage on the load side of the switch on a hot humid August afternoon, observes what might be a loose connection on a screw terminal. Is he going to try to find the breaker, open it, go back to the disco, tighten the screw, then go back to turn on the breaker? Doubt it He or she will likely lean over the top of the condenser to tighten the energized screw, possibly the hand will slip off the screwdriver handle & on to the shank of the driver while he is laying on the grounded metalic cover of the condenser.
I interperet 110.26 to cover fused & non fused discos, and you WOULD be red tagged in my towns. If you do not like my decision, take it to the state, this issue has gone there before.
For the life of me I do not know why this is such a big deal, and why anyone should think the these discos do not require work space. A little communication, a cardboard sign at the discos if they are installed before the condensers, indicating the requirements for a NEC compliant installation. And pay attention to what goes on on your jobs.
I wll not get into the issue of countertop switches & recepts as I agree with Don that this is a poorly written article & needs to be sorted out.
I have seen installations where the disco is behind the condenser & the condenser is so close to the disco it can't be opened for examination even when not energized. Saw another one where the condenser was already in place & the electrician must have been a contortionist to get the disco in a 14" deep space behind the condenser, when the area next to the condenser & behind the wall was wide open.
Rick