I don't think that either of those devices would meet the OSHA rules for the verification that the power has been de-energized.Am interested in your opinion on the RightSwitch / DeadEasy approach.
I don't think that either of those devices would meet the OSHA rules for the verification that the power has been de-energized.Am interested in your opinion on the RightSwitch / DeadEasy approach.
I don't think that either of those devices would meet the OSHA rules for the verification that the power has been de-energized.
I think there is a difference between a lock out for mechanical work and one for electrical work. My comment was based on a lockout for electrical work. There is an OSHA letter interpretation that says the pilot light type devices, even the ones with multiple lamps are not suitable to prove de-energization for electrical work.
The problem with that is I have seen a number of cases where the intent was to lock out P-1-123, but they actually locked out P1-125, and then worked on P1-123. Having a method of proving the correct equipment is locked out at the equipment it critical.
That is exactly why our HOAs bypass all interlocks except the overload relay in the starter.This is the exact problem I'm trying to solve. All it takes is one mistake. To reiterate one of my concerns is as we automate more and more where we have DCS stops and interlocks, the try to start method falls way short. It may be locked out it may be interlocked with DCS? Agreed the pilot light may not be up to snuff, but I have to think its better than what we are doing today. Just my humble opinion.
That is exactly why our HOAs bypass all interlocks except the overload relay in the starter.
Yes, but we do not have much of that type of equipment at the plant where we installed the HOAs.If, for a particular machine, you have operator safety interlocks (proximity, etc.) would you still bypass those in H operation, on the assumption that extra caution would be exercised when using the hand operate control?
Yes, but we do not have much of that type of equipment at the plant where we installed the HOAs.
At first, having just come from a Solar PV board, I wondered how a Home Owners Association came into the LOTO picture.
That is exactly why our HOAs bypass all interlocks except the overload relay in the starter.
Yes the policy at the plant where we installed the HOAs is "try-lock-try". Of course if the equipment is not functional that will not work. The "try-lock-try" is used for mechanical lockouts only. If you are going to work on the electrical, you have to use a meter to prove the equipment is de-energized.
Actually after the lockout we would try the start again before doing the "live dead live"Thanks Don. So in the event of an isolation for electrical work do you use Try Start to match the field equipment to the MCC equipment? So in summary, for each lockout you could:
- Try Start and Confirm Start
- Lockout
- Live Dead Live Check
Our plant started out with the HOA's exactly as stated, where you could use the start to verify the lockout, but as we expanded over the years and installed more and more automation we have departed for the path. I don't think going back is an option but who knows.
I would really like to see some type of "air break" used for lockout, but that is expensive.
The method I would prefer would be a Meltric connection at each motor. It is a plug type of connection and rated for disconnecting under load. You physically remove the power conductors from the motor with this method...absolutely no question that there is no power and that you have the correct motor locked out. However this only really works well for stand alone motors and would be some what difficult for a multi-motor machine.
You don't need to use cables, you can attach LFMC to the Meltric devices.Yes Don this method provides a high integrity and simple isolation but it introduces so many more issues eg:
- Regular people contact with cables
- Damage to plugs and sockets when dropped
- Limited current ranges (approx 250A)
- Perhaps not best for hazardous areas
- Introduced foreign bodies into coupling eg water, non conductive dusts
- Removal of earth conductor to equipment on isolation. Can impact on touch voltages in the event of earth fault on other equipment connected by process connections
- Manual handling issues due to weight of plugs and sockets
- Need to use flexible cables yielding low availability and high cost
- Plug/Socket high cost as you have pointed out
I haven't really noticed what's done at McDonalds in the US but in Australia McDonalds use these sockets that dangle from the ceiling to power machinery. It seems like an ideal solution for this type of environment. Anywhere else though I'm not so sure.
You don't need to use cables, you can attach LFMC to the Meltric devices.
They are hard to damage...much harder than the traditional die cast pin and sleeve devices.
Yes they do have their limits as far as horsepower and current.
They are available in versions listed for Class I, Division 2.
There are caps available to prevent contamination, but of course some one would actually have to apply the cap to the male end. The receptacle cap is self closing.
I guess that there could be a voltage on the equipment in the event of a fault on other equipment, but I don't see that as very likely when we are talking about systems operating at 600 volts or less.
They are not really that heavy.
No need to use cables.
Yes, they are expensive.