- Illinois
- retired electrician
Where does the touch voltage come from after the equipment has been disconnected from its power source? The NEC has no requirements to look at the earth fault loop. The NEC is a prescriptive document and specifies how to install the required bonding and grounding....
On a side note your responses raise a couple of interesting questions:
- Touch voltages on 230VAC systems are a big deal in Australian systems requiring every circuit to have its earth fault loop situation considered. Is that different to NFPA requirements?
- Installing plug/sockets on cables in Australia requires the use of flexible cables rather than building wiring cables. Specifically, greater strand count and more flexible insulation and sheathing. Is that different to NFPA requirements?
Typically the motor would be fed using stranded conductors and liquid tight flexible metal conduit. Adding the Meltric at the motor would not change this. While you can use cables with the Meltric connectors, nothing in the NEC would require you to. If the Meltric is being installed just to provide a local disconnect, it would be my opinion that the NEC would prohibit the use of flexible cable. Our used of flexible cable is very limited.