weressl said:
What the best answer is defined by the nature of the question, not by the location of the discussion. You may point out that the NEC seems to be in conflict with engineering definitions accepted by ANSI, but it is an error on the part of NEC that should be corrected.
You assume an NEC error but why should the NEC CMPs accept a category that spans from 0-600 ? . That span shows a bias in the IEEE toward what is applicable to utilities. . The safety differences between 1v and 600v can't be ignored. .
Both sides would need to make changes to bring about a single standard.
I don't think the NEC CMPs have any desire to classify all voltages under 600 as "low". . IEEE would have to first add a new category for 0-49v. . The NEC would then have to replace their 1000v limit in their system classifications with 600v. . We would need to first know why 1000v was originally chosen.
SYSTEMS / DISTRIBUTION [NEC90.2(A)]
0-49 . . Low . . . . . . [250.20(A), 720]
50-1000 . . Medium . . . . . . [250.20(B)]
1000 & up . . High . . . . . . [250.20(C), examples: 250.180 + 410.140]
For equipment classifications, I don't think there currently is a conflict. . You can overlap IEEE and the NEC equipment categories. . All that is added is a
subcategorizing of 601v-69,000v.
0-600 . . Low . . IEEE
. . 0-600 . . Standard . . NEC equipment [110.26 also see T310.13(A)]
601-69,000 . . Medium . . IEEE
. . 601-2000 . . Low ?High?/Low Industrial . . NEC equipment [110.30 + 490.2]
. . 2001-35,000 . . Medium ?High?/Medium Industrial . . NEC equipment [328.2 def, 328.10]
. . 35,001 & up . . High ?High?/High Industrial . . NEC equipment [example: 450.21(C)]
69,001-230,000 . . High . . IEEE
230,001-800,000 . . Extra High . . IEEE
800,000 & up . . Ultra High . . IEEE
It would also be helpful if IEEE would label the 0-49 range as "low" and use a
different term for 50-600
ELA said:
There is a very real need to catagorize voltage levels relative to your type of work.
I often perform bench testing and want to alert people to a possible hazard. I often put out a sign that states " Caution - High Voltage Hazard" even when there may only be 120 -240Vac present. It is intended to make a point that the area is to be avoided.
Using the phrase "Caution - Extra Low voltage hazard" just does not have the same impact. :grin:
Finally, I don't see what would be accomplished by creating a category break at 120v. . We treat 50v-119v the same as we treat 120v-600v. . If we were in Europe, 120v would mean nothing at all. . Of course in the USA, 120v is the lowest level chosen for household power distribution, but I don't see any advantage in using 120v as a category limit.