I'm glad this thread came up because it not only gives an answer to spark2s question, but also gets the rest of us thinking. . A more accurate answer is always better.
I used to give my students an info sheet that included this:
EQUIPMENT
0-600 . . Standard
601-2000 . . Low Industrial
2001-35,000 . . Medium Industrial
35,001 & up . . High Industrial
SYSTEMS
0-49 . . Low Distribution
50-1000 . . Medium Distribution
1000-4160 . . High Distribution
4160 & up . . Transmission
Now I'm rewriting that section to say this:
EQUIPMENT [NEC90.2(A)]
0-600 . . Standard . . [110.26 also see T310.13(A)]
601-2000 . . Low ?High?/Low Industrial . . [110.30 + 490.2]
2001-35,000 . . Medium ?High?/Medium Industrial . . [328.2 def, 328.10]
35,001 & up . . High ?High?/High Industrial . . [example: 450.21(C)]
SYSTEMS / DISTRIBUTION [NEC90.2(A)]
0-49 . . Low . . . . . . [250.20(A), 720]
50-1000 . . Medium . . . . . . [250.20(B)]
1000 & up . . High . . . . . . [250.20(C), examples: 250.180 + 410.140]
UTILITY / TRANSMISSION [NEC90.2(B)]
as defined in the IEEE standard
0-600 . . Low
601-69,000 . . Medium
69,001-230,000 . . High
230,001-800,000 . . Extra High
800,000 & up . . Ultra High