Your help in resolving a difference of opinion.
For a 4000A feeder, it's my contention that you'd need to use 12 - 600kcmil per phase and a 600kcmil ground in each of the 12 conduits.
A colleague is telling me that you can't do this because by Table 250.122, you need to use an 800kcmil ground (which is no good from a pratical standpoint). I believe the verbage contained in 250.122, (A) would indicate that a 600kcmil grounding conductor would be acceptable. i.e. "but shall not be required to be larger than the circuit conductors supplying the equipment". My colleagues contention is that this does not apply to parallel conductor applications - I don't see why not.
What say you?
For a 4000A feeder, it's my contention that you'd need to use 12 - 600kcmil per phase and a 600kcmil ground in each of the 12 conduits.
A colleague is telling me that you can't do this because by Table 250.122, you need to use an 800kcmil ground (which is no good from a pratical standpoint). I believe the verbage contained in 250.122, (A) would indicate that a 600kcmil grounding conductor would be acceptable. i.e. "but shall not be required to be larger than the circuit conductors supplying the equipment". My colleagues contention is that this does not apply to parallel conductor applications - I don't see why not.
What say you?