1. New 680.22(D) Other Outlets
2. New text
3. (D) Other Outlets. Other outlets containing circuits operating at 30 volts or more shall be not less than 3.0 m (10)ft) from the inside walls of the pool. Measurements shall be determined in accordance with 680.22(A)(6).
FPN: Other outlets may include, but are not limited to remote-control, signaling, fire alarm, and communication circuits.
4. A life safety hazard could arise from the use of other equipment used in the vicinity of a pool.
*Note* I know the substaniation is weak, however I don't have any dead bodies to produce. Just seems like a good idea.
2. New text
3. (D) Other Outlets. Other outlets containing circuits operating at 30 volts or more shall be not less than 3.0 m (10)ft) from the inside walls of the pool. Measurements shall be determined in accordance with 680.22(A)(6).
FPN: Other outlets may include, but are not limited to remote-control, signaling, fire alarm, and communication circuits.
4. A life safety hazard could arise from the use of other equipment used in the vicinity of a pool.
*Note* I know the substaniation is weak, however I don't have any dead bodies to produce. Just seems like a good idea.