I'm inclined to agree. The difference between phase to neutral and phase to ground would seem to infer a fairly significant voltage drop on the neutral.The problem would appear to be an undersized or poorly connected neutral conductor
thank you all for your input, I apologize for the delay on my part for the additional info you are asking for.
Phase to Phase voltage is as follows:
A phase 71A -79A
B Phase: 71A - 79A
C Phase: 56A to 60A
Voltage phase tophase;
A to B = 456V
B to C = 4459
C to A = 458V
We do have an infrared camera...I am not picking up a lot of heat in any panel I have opened so far
I would have put money on that. Happens all the time...................................................................
Just as we suspected earlier, The feed to the MCC was a 3 wire, but from the MCC to the distribution panel it magically became a 4 wire.......
Sounds like that might be rectified by changing the taps. At least the balance looks o.k. thereNow to complicate even further an 1/1/2" conduit with no ground from the distribtuion panel to a sub panel was completely pulled apart about 6 inches...
We are still looking into the low voltage on each phase from froma xfrm fed from this subpanel 45KVA 480 primary 120/208V secondary..A,B, and C phase 108V, 110, and 112V. Xfrm is right above panel that it feeds....