I'm inclined to agree. The difference between phase to neutral and phase to ground would seem to infer a fairly significant voltage drop on the neutral.The problem would appear to be an undersized or poorly connected neutral conductor
I'm inclined to agree. The difference between phase to neutral and phase to ground would seem to infer a fairly significant voltage drop on the neutral.The problem would appear to be an undersized or poorly connected neutral conductor
thank you all for your input, I apologize for the delay on my part for the additional info you are asking for.
Phase to Phase voltage is as follows:
A phase 71A -79A
B Phase: 71A - 79A
C Phase: 56A to 60A
Voltage phase tophase;
A to B = 456V
B to C = 4459
C to A = 458V
We do have an infrared camera...I am not picking up a lot of heat in any panel I have opened so far
I would have put money on that. Happens all the time...................................................................
Just as we suspected earlier, The feed to the MCC was a 3 wire, but from the MCC to the distribution panel it magically became a 4 wire.......
Sounds like that might be rectified by changing the taps. At least the balance looks o.k. thereNow to complicate even further an 1/1/2" conduit with no ground from the distribtuion panel to a sub panel was completely pulled apart about 6 inches...
We are still looking into the low voltage on each phase from froma xfrm fed from this subpanel 45KVA 480 primary 120/208V secondary..A,B, and C phase 108V, 110, and 112V. Xfrm is right above panel that it feeds....