Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
(Another topic no one ever told me in school decades back that an EE would be asked someday....)

A machine shop I hang out at [1] needs to add a small single phase panel after an unfused disconnect that feeds 3ph loads now. The electrician doing the work states the rub is the lug limit. He's not aware of a legal way to terminate more conductors than those there.

My knowledge of the NEC in such an area is roughly “Lasciate ogni speranza, voi ch’entrate!”. If this were not a power system, but something inside a box with various microcontrollers, etc. I'd be thinking of insulated terminal strips, or a soldered Y splice covered with heat shrink, etc.

But it is something NECish. Which if any way should I point the electrician toward to finding an approved solution?



[1] More fun and less likely to get me in trouble than bars -- more toys, fewer calories, and we make fun things.
 

kwired

Electron manager
Location
NE Nebraska
If there is no room to make splices then somehow adding an additional enclosure to make the splices in may be necessary.
 

dkidd

Senior Member
Location
here
Occupation
PE
110.14 (B) Splices. Conductors shall be spliced or joined with
splicing devices identified for the use or by brazing, welding,
or soldering with a fusible metal or alloy. Soldered
splices shall first be spliced or joined so as to be mechanically
and electrically secure without solder and then be
soldered. All splices and joints and the free ends of conductors
shall be covered with an insulation equivalent to that of
the conductors or with an identified insulating device.
 

Besoeker

Senior Member
Location
UK
Do any of you use these for power cables?
Compressionlug_zps92cac186.jpg


They are compression lugs applied with a crimp tool. We'd normally use heat shrink sleeving to cover the end of the conductor and the crimped part of the lug.
 

kwired

Electron manager
Location
NE Nebraska
Are they truly splices... or is this a feeder tap situation. If so, 240.21(B) applies.
Call the connection whatever you want, it is still a connection to another conductor. 240.21(B) only tells us what size of conductor we can use in relation to overcurrent protection in certain circumstances, nothing about how to make the connection though.
 

Smart $

Esteemed Member
Location
Ohio
Do any of you use these for power cables?
Compressionlug_zps92cac186.jpg


They are compression lugs applied with a crimp tool. We'd normally use heat shrink sleeving to cover the end of the conductor and the crimped part of the lug.
Since the advent of polaris-type splice connectors it seems like not many are using these to make splices... but crimping on and bolting several together is just as viable a splice method IMO.
 

kwired

Electron manager
Location
NE Nebraska
Do any of you use these for power cables?
Compressionlug_zps92cac186.jpg


They are compression lugs applied with a crimp tool. We'd normally use heat shrink sleeving to cover the end of the conductor and the crimped part of the lug.

Pretty good chance the OP's disconnect he wants to tie into has factory installed mechanical set screw type lugs. Many are designed or arranged that they are not replaceable with a different design or type - especially in the 200 amp or less device ratings, and is also pretty common (in 200 amp or less devices) that they are designed to only accept one conductor per terminal.
 

Smart $

Esteemed Member
Location
Ohio
Pretty good chance the OP's disconnect he wants to tie into has factory installed mechanical set screw type lugs. Many are designed or arranged that they are not replaceable with a different design or type - especially in the 200 amp or less device ratings, and is also pretty common (in 200 amp or less devices) that they are designed to only accept one conductor per terminal.
So you've never made a splice by crimping on two or more of these terminals and bolting them together? Not even to make up a motor peckerhead?

:blink:
 

kwired

Electron manager
Location
NE Nebraska
So you've never made a splice by crimping on two or more of these terminals and bolting them together? Not even to make up a motor peckerhead?

:blink:
Not to land in a disconnect or on a circuit breaker that has a compression screw lug, especially that lug is not screw/stud fastened and basically is non removable.
 

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
It's there in case someone wants to do it one of those ways... but that does not mean you should.


And I must ask, why don't I want to use a soldered splice? To my thinking, it's the sturdiest, more reliable solution.

Obviously you learned gentlemen do not think so, so please educate me.
I learn by asking people smarter than me both dumb and undumb questions....
 