Timbert
Member
- Location
- Makawao, Hawaii
Get yourself a copy of NFPA 79 (you can view it online for free at NFPA.org but you should get a copy as this guy is gonna become your best buddy). Chapter 6 Protection from Electric Shock is what you want to read.
Now, there is no defined you will use a x style limited switch, connected to y type disconnect device monitored by a z. There are just way too many possible solutions to this problem.
You could also look into IEC 62061, the international machine safety standard. This standard includes methods for analyzing how 'safe' a particular solution is.
I would also try to educate the customer on what is required i.e. at 48vdc this type of interlocking is not required. It will add expense and complexity with little additional safety benefit and might even lull them into a false sense of security. If you overuse a complex safety technique for extra low voltage, when someone opens up a cabinet with MV in it they will think "business as usual." Just an opinion, if the customer insists then go right ahead. But there are appropriate levels of safety. I would not use a trapped key to keep someone out of 48vdc.
6.2.3 Enclosure Interlocking. When required by 5.3.1.4, each disconnecting means mounted with or adjacent to a control enclosure that contains live parts operating at 50 volts ac (rms value) or 60 volts dc or more shall be mechanically or electrically interlocked, or both, with the control enclosure doors so that none of the doors open unless the power is disconnected. Interlocking shall be reactivated automatically when all the doors are closed.
Now, there is no defined you will use a x style limited switch, connected to y type disconnect device monitored by a z. There are just way too many possible solutions to this problem.
You could also look into IEC 62061, the international machine safety standard. This standard includes methods for analyzing how 'safe' a particular solution is.
I would also try to educate the customer on what is required i.e. at 48vdc this type of interlocking is not required. It will add expense and complexity with little additional safety benefit and might even lull them into a false sense of security. If you overuse a complex safety technique for extra low voltage, when someone opens up a cabinet with MV in it they will think "business as usual." Just an opinion, if the customer insists then go right ahead. But there are appropriate levels of safety. I would not use a trapped key to keep someone out of 48vdc.