mivey
Senior Member
Cool! Thanks!I will look for the comments on that PI later.
Cool! Thanks!I will look for the comments on that PI later.
Found it: Public Input No. 4224-NFPA 70-2014
(1) Readily Accessible Location.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
( A ) Where installed on one family and two family dwellings, the service disconnecting means shall be installed outside the structure at the nearest point of entrance of the service conductors.
Statement of Problem and Substantiation for Public Input
Statement of Problem
Access to the service disconnecting means for first responders is very challenging when the disconnect is installed in a basement. Additionally with the incorporation of distributed generation such as PV or energy storage devices, the lack of access to safely securing the power generation to a residence from the exterior is made even more challenging.
The installation of a utility external service disconnect is a common practice in many areas of the country, including corrosive coastal environments, and should be provided in the code to ensure the safety of first responders when service disconnection is required in an emergency
This proposal seeks to require the installation of a utility external AC disconnect at the location of the meter on the exterior of the structure.
Submitter Information Verification
Submitter Full Name: Matthew Paiss
Organization:
Affilliation: International Association of Fire Fighters
Street Address:
City:
State:
Zip:
Submittal Date: Thu Nov 06 15:09:10 EST 2014
Committee Statement
Resolution: This requirement is onerous and not necessary. The hazard in a one or two family dwelling than it is not greater than in a multi-family dwelling or commercial building. The statement relative to environmental impact on exterior service disconnects is incorrect and in fact there are many instances where exterior disconnects do not operate when utilized due to the effects of the atmosphere on the disconnect. The submitter has not presented and factual data to support this requirement. Onsite power production sources have their own requirements relative to disconnecting means, anti-islanding features and proper placarding and notification relative to their presence on the property.
What you say is true and yet over simplified. Outside disconnect is not required "if" we wish to place the panel with main nearest the point of entrace of service conductors.
That's why I can go in a sub-division of 5 thoundand homes and everyone of them will have a meter main combo. The may have figured that it was more cost effective to place the panel at a better location to feed branch circuits.
I didn't make myself clear when I said required. I should have said required because of panel location ( which does give them a choice ). I kind of assumed that people would know this.
Well, this is going of topic... but I remember a study done by the NFPA that said most breaker failures occur where breakers are installed outside.
Well, this is going of topic... but I remember a study done by the NFPA that said most breaker failures occur where breakers are installed outside.
Here in CA, most residential panels are installed outdoors, and I would almost willing to bet that there are more varied climates then other states, coastal, desert, snow, etc., doubt it's that much of a problem.
Here in CA, most residential panels are installed outdoors, and I would almost willing to bet that there are more varied climates then other states, coastal, desert, snow, etc., doubt it's that much of a problem.
Pretty sure the utility in CA requires outside disconnects already. At least in some case, I have seen the requirements posted on these forums before
Pretty sure the utility in CA requires outside disconnects already. At least in some case, I have seen the requirements posted on these forums before
Pretty sure the utility in CA requires outside disconnects already. At least in some case, I have seen the requirements posted on these forums before
I believe that it's a EUSERC requirement you're referring to and it applies to just about all western states that have adopted EUSERC.
No, there where discussions of CA services, specifically the practice of running the service conduit inside the wall cavity.
Someone posted one of the power company spec sheets and it showed the service conduit going directly into an exterior meter main.
Alright, but I still stand by my statement that it's a EUSERC requirement, at least for residential services.![]()
Wouldn't that be the same as NESC, a standard they can chose to ignore or follow at will?