mastlog
Member
- Location
- Jeddah Saudi Arabia
Good day Guys,
I have an MCC with 11 starters (DOL) each 7.5KW and as per datasheet LRA = 102.85 A and FLA = 14.4 A.
I need to size the main breaker for those starters.
So what i did actually. simply calculate the total FLA which will be 14.4 x 11 = 158.4 A. And keeping in view the 120% rule which makes 189.6 A.
So i selected 200A breaker for the mains incomer.
Can some body validate the calculation. Or i need to consider other factors too.
Thanks in anticipation.
I have an MCC with 11 starters (DOL) each 7.5KW and as per datasheet LRA = 102.85 A and FLA = 14.4 A.
I need to size the main breaker for those starters.
So what i did actually. simply calculate the total FLA which will be 14.4 x 11 = 158.4 A. And keeping in view the 120% rule which makes 189.6 A.
So i selected 200A breaker for the mains incomer.
Can some body validate the calculation. Or i need to consider other factors too.
Thanks in anticipation.