Main breaker terminal covers required?

Status
Not open for further replies.

Christoph

Master Electrician, Code Official
Location
Coopersburg, PA
Occupation
Electrical Inspector
Hello,

I am inspecting a job with a lot of sub panels (70) and on one of them they had the rubber protectors installed on the line side of the MCB. Made me wonder if they are required. I consulted with others in my agency and they said they believed it was required. I looked at 110.27 and 408.3 and could not come up with the requirement. My other instinct was 110.3(B). If the manufacturer tells you to put them on, put them on, right? Any experience and code references? This is 2014 NEC. (Job has been going for a while).
 
230.62C of the 2020 NEC has a requirement, I'm not sure what the 2014 requires


(C) Barriers


Barriers shall be placed in service equipment such that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
Share url icon
 
That’s just service equipment though. If he has 70 sub panels they won’t need it. Although I think it was added to the 2023 for all other equipment terminals.
 