We have a client that had a new building (911 center) built two years ago. I know nothing about the original project beyond that.
In the last year their main breaker has tripped twice (including once a couple weeks ago, in the middle of the night). They have asked their neighbors if they have experienced any issues, they said not really - they installed some surge arrestors to take care of some power quality issues, but nothing that tripped a breaker. The utility does not see anything unusual on their end. The EC thinks it may be an issue with the breaker and recommends removing and testing the breaker.
In the absence of any more information I tend to assume the people closest to the situation know it best - so I would tend to say "whatever the EC says". It is a five-hour drive from my office and I don't believe our firm did the original engineering on this. That said, what questions could I toss out there? I've got:
1. Have you consulted with the engineer of record?
2. Does the facility have ground fault protection? Is the main tripping, or is it the GFP?
3. What kind of power quality issues was the neighbor experiencing?
4. What kind of loads within the building could run at night? Was the facility occupied? (I can't imagine what might cause it.)
5. Ask for copy of riser, motor list, original service calcs, and OCPD study.
6. Did the first trip also occur at night?
Anything else?
In the last year their main breaker has tripped twice (including once a couple weeks ago, in the middle of the night). They have asked their neighbors if they have experienced any issues, they said not really - they installed some surge arrestors to take care of some power quality issues, but nothing that tripped a breaker. The utility does not see anything unusual on their end. The EC thinks it may be an issue with the breaker and recommends removing and testing the breaker.
In the absence of any more information I tend to assume the people closest to the situation know it best - so I would tend to say "whatever the EC says". It is a five-hour drive from my office and I don't believe our firm did the original engineering on this. That said, what questions could I toss out there? I've got:
1. Have you consulted with the engineer of record?
2. Does the facility have ground fault protection? Is the main tripping, or is it the GFP?
3. What kind of power quality issues was the neighbor experiencing?
4. What kind of loads within the building could run at night? Was the facility occupied? (I can't imagine what might cause it.)
5. Ask for copy of riser, motor list, original service calcs, and OCPD study.
6. Did the first trip also occur at night?
Anything else?