Main Circuit Breaker Ampacity

Status
Not open for further replies.

SMB

Member
This is an easy one that I can't seem to remember. What formula do you use to determine the MCB ampacity of a panelboard? Is it 100% of non-continuous loads + 1.25% of continuous?

Thanks
 

jbt260

Member
Location
Ohio
Occupation
Electrical Engineer
SMB said:
This is an easy one that I can't seem to remember. What formula do you use to determine the MCB ampacity of a panelboard? Is it 100% of non-continuous loads + 1.25% of continuous?

You are correct, except it's 125% of continuous. Don't forget to consider non-simultaneous loads and demand factors.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Is the overcurrent protection device providing protection for just the panelboard?

Take a look at 408.36 for overcurrent protection requirements for panelboards.

Also take a look at 215.3 for overcurrent protection for feeders.

Chris
 

bob

Senior Member
Location
Alabama
SMB said:
This is an easy one that I can't seem to remember. What formula do you use to determine the MCB ampacity of a panelboard? Is it 100% of non-continuous loads + 1.25% of continuous?

Thanks
The max MCB is the rating of the panel board.
 