Main Circuit Breaker Ampacity
SMB
This is an easy one that I can't seem to remember. What formula do you use to determine the MCB ampacity of a panelboard? Is it 100% of non-continuous loads + 1.25% of continuous?
Thanks
You are correct, except it's 125% of continuous. Don't forget to consider non-simultaneous loads and demand factors.
Is the overcurrent protection device providing protection for just the panelboard?
Take a look at 408.36 for overcurrent protection requirements for panelboards.
Also take a look at 215.3 for overcurrent protection for feeders.
Chris
Thanks
The max MCB is the rating of the panel board.