cutlass

New member
if youhave 8 meters and each one has a 100 amp main breaker do you have to fuse the main for the whole service
 

radiopet

Senior Member
Location
Spotsylvania, VA
I think he is asking a [230.71 & 230.72] question in regards to grouping and maximum disconnects...versus the load served for the system...but then again I am not sure.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
It looks like he's asking what size fuse to put in the service disconnect when there are eight 100A breakers on the load side of it, but I could be mistaken. Perhaps Cutlass will elaborate a bit more.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
It looks like he's asking what size fuse to put in the service disconnect when there are eight 100A breakers on the load side of it, but I could be mistaken. Perhaps Cutlass will elaborate a bit more.

I think the question is, do you need to fuse the disconnect for the whole service or can it just be a non fused disconnect.
 