So this is my first one of these I ever installed, https://platt.com/platt-electric-su...iance-Controls/A310A/product.aspx?zpid=178075
It came with a built in power inlet not hocked up. I don't see in 702 any requirements that the inlet has to be outside.
Instruction says " The inlet is supplied separately for indoor models to encourage the use of a remote connection outdoors reducing the likelihood of running the generator indoors which is extremely dangerous."
Nothing say it can't be. Is there something in black and white that forbids this?
Inspector said he won't approve it. Its an easy fix, I assumed since it was part of a listed assembly that it would be compliant on there end.
I called them and said They include it for the homeowner, but they can't install it cause its in violation of UL1008. Have not had time to read this.
If it's in violation why Include it.
I am sure this is a dumb question and you will easily show me were I overlooked that I can't do this.
It came with a built in power inlet not hocked up. I don't see in 702 any requirements that the inlet has to be outside.
Instruction says " The inlet is supplied separately for indoor models to encourage the use of a remote connection outdoors reducing the likelihood of running the generator indoors which is extremely dangerous."
Nothing say it can't be. Is there something in black and white that forbids this?
Inspector said he won't approve it. Its an easy fix, I assumed since it was part of a listed assembly that it would be compliant on there end.
I called them and said They include it for the homeowner, but they can't install it cause its in violation of UL1008. Have not had time to read this.
If it's in violation why Include it.
I am sure this is a dumb question and you will easily show me were I overlooked that I can't do this.