180509-1957 EDT
ptonsparky:
Back to rereading your post #12.
Apparently you have only a low level limit. Not to confuse things, but it is the high limit. Incoming product covers it somewhat before things empty out. Once product drops below it there is an additional time delay that ends up to be about 3 minutes before the input motor starts.
1. When low level is reached, then supply motor starts. After timer delay.
2. At this start time it will be 3 minutes before any new stock flows into the tank. Is it really true that this 3 minutes is a constant independent of input flow rate? We will assume it is. the 3 minutes is dependent on the outflow. Assume it is constant for now.
3. For 3 minutes there is an out flow of product. Thus, the product in the tank has been reduced from the low level by 3*Fo. The flow out of the tank is continuous. Only the inflow cycles. Off at the high limit and On after the timer sequence
4. The time to get back to the low limit or motor pump up time is
T = 3*Fo / (Fi - Fo) = 3 / (Fi/Fo - 1).
If Fi = 2*Fo, then 3 minutes.
If Fi = 1.1*Fo, then 30 minutes.
If Fi = 4*Fo, then 1 minute.
.