Expanding on my post #42 of yesterday.
I believe my suggestion of that post can reduce your level variation, min max level vs time, by some substantial value if the method has no impact on your loss of steam problem.
Some assumptions:
1. The single point level sensor has no inherent hysteresis at its threshold level point, and that its ability to sense the average tank level at that threshold is a small fraction of the min to max level variation achieved with your present 3 minute no input feed time method (full on-off control of the input feed rate). Mechanical hysteresis would be no problem, but is not required.
2. By my two input feed rate method there is no increase in the steam loss problem.
3. By using the PLC to switch the input feed rate between two rates has no effect on the lifetime of the equipment. Thus, fast slow cycling can be a shirt time cycle.
4. Feed rates specified by the PLC are close to the actual process feed rates. May not matter too much, but probably. can be monitored by the activity of the level threshold sensor activity.
5. Separate means are included in the PLC to protect from abnormal conditions.
This system can be made to servo from your programmed output feed rate by simple delta values used to create the fast and slow input feed rates. Thus, a single value can be adjusted to determine cooking time.
If there is short time oscillation of the output of the level threshold sensor at the sensing point, then some amount of on or off or both time delay may be required from the sensor. In other words a low pass filter. This creates a type of hysteresis based on time rather than level.
.