Doing some calculations and my mind drew a blank on this one for some reason.Couldnt find the exact answer in the nec.Could anyone help me out?
I would hate to have to pull 15 # 12 in an 3/4 conduit.celtic said:Table C-10 shows 15
William1978 said:I would hate to have to pull 15 # 12 in an 3/4 conduit.
William1978 said:I would hate to have to pull 15 # 12 in an 3/4 conduit.
I didn't see where a 20A CB was a concern.iwire said:I agree and once you apply derating they will not support a 20 amp breaker any longer.
celtic said:I didn't see where a 20A CB was a concern.
Pierre C Belarge said:NYC test question on the test provided earlier today.
What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?
iwire said:Your right, the wires will probably not be connected to anything at all. :wink:
I figured the basic question had been answered and I would elaborate.
Pierre C Belarge said:NYC test question on the test provided earlier today.
What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?
2450'Pierre C Belarge said:NYC test question on the test provided earlier today.
What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?
infinity said:It would be tough to word that question more poorly.
Pierre C Belarge said:What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?
Pierre C Belarge said:NYC test question on the test provided earlier today.
What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?