maximum amount of #12 wires to fit into 3/4" pvc pipe?

Status
Not open for further replies.
Doing some calculations and my mind drew a blank on this one for some reason.Couldnt find the exact answer in the nec.Could anyone help me out?
 

iwire

Moderator
Staff member
Location
Massachusetts
celtic said:
I didn't see where a 20A CB was a concern.

Your right, the wires will probably not be connected to anything at all. :wink:

I figured the basic question had been answered and I would elaborate.
 

Buck Parrish

Senior Member
Location
NC & IN
Pierre C Belarge said:
NYC test question on the test provided earlier today.


What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?


Is their a -
None of the above- answer.
 

celtic

Senior Member
Location
NJ
iwire said:
Your right, the wires will probably not be connected to anything at all. :wink:

I figured the basic question had been answered and I would elaborate.


You're right....how long is the OP's conduit again? :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Pierre C Belarge said:
NYC test question on the test provided earlier today.


What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?


It would be tough to word that question more poorly. :rolleyes:
 

celtic

Senior Member
Location
NJ
Pierre C Belarge said:
NYC test question on the test provided earlier today.


What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?
2450'

How'd i do?

:D
 

celtic

Senior Member
Location
NJ
infinity said:
It would be tough to word that question more poorly. :rolleyes:

Maybe break it down by color....

What is the total length of Green 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?

:D:D:D
 

iwire

Moderator
Staff member
Location
Massachusetts
Pierre C Belarge said:
NYC test question on the test provided earlier today.


What is the total length of 10 AWG, Type THHN conductors that can be installed in a 70 foot length of EMT?

Seems straight foward to me, 700' without looking in the book.

10 x 70' = 700'
 