40 amps only in the whole solar system... wow thats pretty small for such a big place. :roll:
It has a very high efficiency rating.![]()
Thanks Don for the NEC reference. Suppose i needed a larger breaker because the output from the inverter is greater than 40amps. What's the best/allowable method of tying it into the
200amp main breaker panel?
What is your inverter? The breaker size is the maximum continuous rated output current of the inverter X 1.25, and then up to the next standard breaker size. If that comes out to be more than 40A, then you'll have to come up with a Plan B.Thanks Don for the NEC reference. Suppose i needed a larger breaker because the output from the inverter is greater than 40amps. What's the best/allowable method of tying it into the
One thing you can do is use a smaller backfed breaker,
You can install a smaller main breaker in your service panel to generate more headroom (ditto on the electrician),
However you do it, you must always be certain the the rating on the breaker is lower than the derated ampacity of the conductors which feed it.
I thought you could go smaller but not larger, but I'll stand corrected in lieu of running for the code book. ;^)[Using a smaller backfed breaker] would be a code violation.
We covered that.You can also downsize the main breaker to a 175amp if you do a load check for the residence and do not surpass the 80% rule and if your AHJ is ok with it. If you did that you could use a 65amp breaker.
Also the poster is an electrical contractor, not a DIY.
I thought I'd gotten into an argument with someone else on this very subject and the conclusion was you could ALWAYS go smaller unless the size was =specifically= required by some section of the code. For example, the 20A SABCs in a kitchen.
On the basis of that, I call "CODE SECTION!"
Ampacity and Overcurrent Device Ratings. Photovoltaic
system currents shall be considered to be continuous.
(1) Overcurrent Devices. Overcurrent devices, where required,
shall be rated as required by 690.8(B)(1)(a) through
(1)(d).
(a) To carry not less than 125 percent of the maximum
currents calculated in 690.8(A).
Inverter Output Circuit Current. The maximum current
shall be the inverter continuous output current rating.
Yes, but an electrical contractor isn't a licensed electrician![]()