I believe that SG-1 was drawing waveforms for a '2-phase' (90 degree phase offset) 3 wire system.
If I understand his point, under the naming scheme used by the NEC where a two leg 120/208 service is called a single phase service, such a 2 leg 2 phase service would also be called single phase.
I disagree, not because the physics analogy is not correct, but because of how the two are used. Three wires, one grounded, with a phase offset between the ungrounded conductors of either 90 or 120 degrees; seems pretty similar to me...simply that they have different _uses_.
Two leg 120/208 is used for residential applications where ordinary 120/240 single phase might otherwise be used, but where you have lots of such users (apartment buildings and the like) and want to provide balanced loading to the three phase distribution system. You don't need a 'rotating field producing' phase offset.
Two leg '2 phase' is an old system used for industrial applications such as running motors, where you explicitly want a phase offset that can produce a rotating field.
-Jon