mivey
Senior Member
But pretty much so."Independent from each other" strikes me as a poor choice of words. I think your point is that they differ. But as long as they are derived from the same HV primary phase (or as gar pointed out, the same generator shaft), then they aren't entirely independent.
Re-think that.I also disagree with you about the L1 and L2 loads not being in series. It is only on the assumption that the resistance of the N conductor is negligible that you can ignore how they are in series.
Trace a current path from L1->line#1wire->load#1->neutral#1wire->N
Then a current path from N->neutral#2wire->load#2->line#2wire->L2
Why would you ever think the current for load#1 would ever jump from load#1->load#2?
The neutral conductors and tie to the N terminal makes them not in series and the more the loads differ the more apparent that becomes.
Only by opening the neutral do they become a series circuit. You might could say the same applies for a perfect load match and perfect winding match but that would be an extreme cases.