wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Hmm, I don't see how that would be non-compliant, it would still fit 725.136(I), as all of the ELP conductors are within a metal-clad cable.I didn't say anything about 725.136. What I will say is that 725.136(I) permits MC-PCS. However, if you ran a separate MC cable and a Class 2 or 3 cable in wiremold without a divider, I'd say it was non-compliant under 725.136.
There is an odd difference between 725.136 and 800.133(A), in that both end with a section called "Other Applications" with very similar language, but 800.133(A) has an earlier section covering raceways, while 725.136 does not. So if section headings limit the scope of a section, then 800.133(A) "Other Applications" only applies outside a raceway (or enclosure, etc), while 725.136 "Other Applications" can apply within a raceway.
I'm unsure where I fall on this issue. One further observation: 725.136(A) starts off "Cables and conductors . . . shall not be placed" while 800.133(A)(1)(d) states "Communications conductors shall not be placed . . . with conductors of electric light, power, . . ." So if we are to believe that every difference between 725.136 and 800.133(A) is intentional, this would suggest that 800.133(A)(1)(d) is making a distinction between cables and conductors.
Cheers, Wayne