I see that. I was going by circuits at the end of the sentence. Nevertheless, I still read it as saying we cannot place both types in the same raceway, regardless of either being in a cable. Would you prefer it say cable or conductors? I look at a cable assembly of conductors within a raceway to be no different than single conductors within a raceway.
Smart$:
So if someone ran rigid steel conduit through a surface metal wireway, and that RGS has power conductors in it, we can't put data cables in the same wireway?
That seems to be your conclusion when you say a raceway with conductors is no different than MC cable.
That seems to conflict with what you said here:
The armor of MC is not a permanent barrier or listed divider.
I would completely consider it a permanent, listed divider. That's why MC cable is a Chapter 3 wiring method.