330.10(A)(12)In wet locations where any of the following conditions are met:
a.The metallic covering is impervious to moisture.
b.A lead sheath or moisture-impervious jacket is provided under the metal covering.
c.The insulated conductors under the metallic covering are listed for use in wet locations.
Minuteman said:Why is it, that there are no listed rain tight MC connectors? Or at least not that my suppliers are aware of.![]()
Pierre C Belarge said:I am not sure the MC cable they are saying as permitted for outdoor use would be the "common" type we generally see in the supplyhouse.
330.10(A)(12)In wet locations where any of the following conditions are met:
a.The metallic covering is impervious to moisture.
b.A lead sheath or moisture-impervious jacket is provided under the metal covering.
c.The insulated conductors under the metallic covering are listed for use in wet locations.
Pierre C Belarge said:I am not sure the MC cable they are saying as permitted for outdoor use would be the "common" type we generally see in the supplyhouse.
There are 3 types of MC cable.
The type we generally see I do not believe is listed for wet locations unless it has the nonmetallic sheathing.
There is:
"Smooth Sheath Type" - rarely used by the general electrician
"Corrugated Sheath Type" - again rarely used by the general electrician
"Interlocked Type" - this is the type of MC cable used daily by electricians.
I do not believe this Type is permitted for outdoor use without the nonmetallic sheathing such as we see for "parking garage" Type MC.
I think that it takes a little investigation to get to the bottom of this.
*330.116 - read the first sentence.
*(PJAZ) , page-230 of the 2007 UL White Book.
*Manufacturer's websites/product manuals.
I would have to disagree here Pierre. Art 330.10 (11) is pretty clear. If any of the following conditions are met then MC is permitted. It does not say a specific type is permitted.Pierre C Belarge said:I am not sure the MC cable they are saying as permitted for outdoor use would be the "common" type we generally see in the supplyhouse.
iwire said:Under 2005 NEC MC can be run in wet locations, not sure if that changed for 2008.
Here it is from 330.10 2002 NEC
480sparky said:It's changed to 330.10(A)(11), and (c) has the additional verbage of: "and a corrsosion-resistant jacket is provided over the metallic sheath ."
Pierre C Belarge said:Now to really open a can of worms...you know I just hate doing this.:grin:
If the jurisdiction I am in does not refer to the 2008, how do I handle this for installation/inspection purposes???
Pierre C Belarge said:Now to really open a can of worms...you know I just hate doing this.:grin:
If the jurisdiction I am in does not refer to the 2008, how do I handle this for installation/inspection purposes???
iwire said:You know darn well what you have to do, you are obligated to enforce only the adopted codes.
Do you see a lot of MC run outside?![]()
iwire said:You know darn well what you have to do, you are obligated to enforce only the adopted codes.
![]()
iwire said:Thats darn nice, but that is a voluntary choice. :smile:
You can't expect to show up at a job and tell the EC that you decided the 2008 will be used.