F frea New User Location Elkton Maryland Nov 29, 2018 #1 Seems like this isn't allowable but can I terminate 12 AWG MC cable into a cord body? 120/240 volt circuits.:slaphead:
Seems like this isn't allowable but can I terminate 12 AWG MC cable into a cord body? 120/240 volt circuits.:slaphead:
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Nov 29, 2018 #2 No you can not. 330.40 says fittings have to be listed and identified for such use. Welcome to the forum.
No you can not. 330.40 says fittings have to be listed and identified for such use. Welcome to the forum.
G GentekPower Member Location Michigan Nov 29, 2018 #3 Not to mention that if you even tug on MC the wrong way after it's secured into a cord end like that, the jacket will pop open and expose the wires.
Not to mention that if you even tug on MC the wrong way after it's secured into a cord end like that, the jacket will pop open and expose the wires.