Because it's Vitalink 2-hour rated MC cable that he's asking about.Maybe a dumb question, but why MC instead of pulling wire through a pipe when it's this much work to pull it?
500s aren't exactly easy just as THHNs, but 30 guys aren't needed for a basic 500 pull either.
You'll have to forgive me, MC is verboten in much of my area.Because it's Vitalink 2-hour rated MC cable that he's asking about.
I would plan on 8-10. Besides being heavy it's simply hard to handle.So for my situation( 400' run) could that be done with 4 guys?
Ok THANKS a lot. can you explain the setup/task of these 8-10 men? E.g. 2 feeding, 2 pulling etc.I would plan on 8-10. Besides being heavy it's simply hard to handle.
Thank you.The way I would plan or estimate is have three or four at the reel, two at the tugger, and three or more watching the rollers and roaming.
I wish I could. One thing I truly regret is not going through the apprenticeship program with my union. mike Holt is my education. I truly grateful for you guys.Don't take this wrong, but if you get the project go help the crew during the installation
One last thing I think lol do you think it makes sense or is practical to put a 450 ft run on one reel?Don't take this wrong, but if you get the project go help the crew during the installation
If it's a 4/C it will be, If it's individual conductors it's 6 one 1/2 dozen the other. A single roll will speed up set up time.One last thing I think lol do you think it makes sense or is practical to put a 450 ft run on one reel?
Regarding the four conductor reel that must be one ginormous reel. Is there any type of electric pallet jack that could move that around?If it's a 4/C it will be, If it's individual conductors it's 6 one 1/2 dozen the other. A single roll will speed up set up time.
Regarding the four conductor reel that must be one ginormous reel. Is there any type of electric pallet jack that could move that around?
1000%. They are considering going to 1/C.
Are you sure this is a 4 conductor cable?
LOL. Do you remember( or know) if you could run 380' horizontally without having to splice?That pallet jacket is rated for 5500 pounds but we've moved 8000 pound transformers with it. I've had the (dis)pleasure of running a lot of Vitalink and I would opt for the single conductor type if it's 500 kcmil.