Mc cable

Status
Not open for further replies.

jmsbrush

Senior Member
Location
Central Florida
There is a dry wall ceiling, coming down the from the drywall ceiling there is MC cable going down 1.5' to an automatic door. We use mc cable because there was no way to run it in emt.
There is no attic space either.
So we were able to fish the mc cable from another power source near by.
The customer said he doesn't want to see the mc, he would rather see emt,
with this being said. Can I sleeve the mc cable with a piece of emt?
 
330.10(A)

General uses. Type MC cable shall be permitted as follows:

(7) In any raceway.
 
That brings a question from me. Does anyone see a problem with pulling the back out of 700 series Wiremold and using it for physical protection in a situation like this?

No, but unless the AHJ approves the use of 700 wiremold for protection from physical damage it is nothing more than a way to cover the MC cable so it is not visable.

Chris
 
Can I sleeve the mc cable with a piece of emt?


Like anything else, someone, somewhere will give a reason why you can't........but I do it often. As long as the EMT is grounded/bonded it's safe and looks beter.
 
No, but unless the AHJ approves the use of 700 wiremold for protection from physical damage it is nothing more than a way to cover the MC cable so it is not visable.
Which should be more than adequate near the ceiling, and is what the OP's customer wants.

Would it be acceptable to insert the MC into the surface raceway without using a termination fitting?
As a sleeve, yes, but the MC still needs to be properly terminated with fittings at both ends.
 
Agreed, but my point is that the only person that can determine if it is adequate for protecting the MC from physical damage is the AHJ.

Chris


No he is not the only one who can determine this. Many of us can make this determination but he gets the final say--unfortunately:D:D
 
And mine was that it may not need physical protection.

And I agree. A section of MC cable up high comming out of a ceiling IMHO would not be subject to physical damage but my opinon does not matter. The oonly opinion that matters on this is that of the AHJ.;)

Chris
 