It's been discussed to death, Joe T will tell you it is a violation, I do not agree.
I noticed that after that "Discussion" Joe T has only commented on this sight infrequently. :roll:
It's been discussed to death, Joe T will tell you it is a violation, I do not agree.
How much is an EMT connector a conduit coupling and a MC duplex? I bet half of $5 or less.
IMO going down that road also means we can not strip NM to go into panels.
My only concern with this set up is ,.. that it has not been evaluated for it's ability to reliably handle a fault current ..
You should not, they print false info pretty often.
You lost me here. If the job is inspected the inspector will see the NM/conductors before they enter the panel.
All three parts have been evaluated for carrying fault current.
Not sure they have in this configuration ,.. I have found that they are a crappy connection , and loosen quite easily , JMO
What about the marking on the wires?
Is'nt this why NM can't be striped and the conductors used?
I know this has been discussed to death.
IMO going down that road also means we can not strip NM to go into panels.
Not sure they have in this configuration ,.. I have found that they are a crappy connection , and loosen quite easily , JMO
I find a lot of things that have passed grounding test appear to have poor connections.
Push in MC connectors and reducing washers come to mind but both pass ground fault testing
I'm just not sure the connections provide for a good fault current path