MCAP cable must be used with UL Listed fittings designed to accomodate the cable. As far as I know, there are no MCAP cable fittings made for ENT or PVC systems. So, transitioning from MCAP to anything plastic should be done in a metal J/B and with approved MCAP metal fittings. When used this way, the AL EGC would be trimmed flush with the MCAP sheath as per the mfr's instructions. Then copper EGC and appropriate conductors should be fished from the metal J/B down the ENT into the plastic box.
 